Hi,

 

I'm using the Modbus TCP interface to read data from a number of Schneider ION and PowerLogic meters. For the bulk of the data it has gone reasonable smoothly; I've built some nice AF templates that configure all the tags nicely. There is one set of tags however that is giving me a bit of a headache. These are the energy accumulators (real energy in, real energy out, ....). According to the Schneider documentation these values have a data type of Mod10. Mod10 is really just four registers that are combined in the following manner (R? = register ?):

     R4 * 1,000,000,000,000 + R3*100,000,000 +R2* 10,000 +R1

 

While I could read each of the four registers as 16 UINT (16 bit unsigned integers) and then use AF Analytics to perform the calculation. I would prefer not to do this for a number of reasons; a lot of additional tags (I have 4 Mod 10 tags per meter and about 300 meters on one site - 4,800 intermediate tags on one site) and the additional load on AF Analytics. So before I dive down the easy hole I would like to inquire if anyone know how to read Mod10 values directly within the PI Modbus interface?